  • in reply to: Experience of blade failure #2412
    Marcel Grinwis
    Participant

    Thank you for this information. We do have a fan guard but I’m worried this would not hold the impact of the blade, am I overestimated the force of the blade?

    in reply to: Experience of blade failure #2389
    Marcel Grinwis
    Participant

    Thank you for the information this is much appreciated, we have a A frame ACC.

    in reply to: Experience of blade failure #2386
    Marcel Grinwis
    Participant

    Hello All,

    Thank you for the responses. We are planning on exchanging all blades but of course there is a lead time of multiple weeks and on top of that the repair time. We expect the blades will last long enough to exchange all blades, but we would like to known the impact if one would fail. Risk= likelihood x consequence.

    @powerplantdocs
    , thank you for the response about the vibration this is very helpful.
    I understand the other blades will get damaged if one would fail, is there any experience with a blade damaging the structure or the condensor tubes?