ACC Users Group › ACC Users Group Discussion Forums › Fans & Gearboxes › Locking fans for safety
- This topic has 9 replies, 8 voices, and was last updated 7 years, 9 months ago by udhay61.
-
AuthorPosts
-
-
January 19, 2017 at 1:16 pm #1643yefimParticipant
I would like to know how do users lock their ACC fans to prevent self-spinning during maintenance. This came up as a safety item, and our fans don’t seem to have design provisions for that. I would appreciate any suggestions ACC Users may provide.
-
January 19, 2017 at 3:03 pm #1644vahidjohnParticipant
At our site we use a strap and wrap one end to a blade and the other end to a fixed support like a railing. This is very effective in preventing self spinning
-
January 19, 2017 at 3:36 pm #1645guyrenParticipant
We lock out tag out the motor then use a good quality 3/8″ rope and tie one blade in one direction and a second blade in the opposite direction. Ropes tied to the structure.
We’ve also used two ropes on one blade in either direction to structure. Our blades are difficult to reach as they are several feet below the deck so we make a lasoo in the rope to catch the blade. -
January 19, 2017 at 5:44 pm #1646Martin CyrParticipant
I would agree with the use of a 2-3″ wide strap looped over the end of the blade and tied off to the motor bridge handrail or some other visible place. As an added equipment safety measure a LOTO tag should be applied to the strap as part of the LOTO to ensure that the strap is removed before the fan is returned to service.
I’ve also witnessed some facilities utilize a large, 2 piece, pipe clamp, with extended length that is bolted to the motor drive shaft after the guards are removed. The extended length of the pipe clamp would then contact the yoke area on the motor (as applicable).
Not all fan motor/gearbox will have this sort of access so the easiest and quickest means of securing fan blades
-
January 19, 2017 at 5:45 pm #1647Martin CyrParticipant
I would agree with the use of a 2-3″ wide strap looped over the end of the blade and tied off to the motor bridge handrail or some other visible place. As an added equipment safety measure a LOTO tag should be applied to the strap and be recorded as part of the LOTO to ensure that the strap is removed before the fan is returned to service.I’ve also witnessed some facilities utilize a large, 2 piece, pipe clamp, with extended length that is bolted to the motor drive shaft after the guards are removed. The extended length of the pipe clamp would then contact the yoke area on the motor (as applicable).
Not all fan motor/gearbox will have this sort of access so the easiest and quickest means of securing fan blades
- This reply was modified 7 years, 9 months ago by Martin Cyr. Reason: duplicate
-
January 19, 2017 at 9:52 pm #1649AnonymousInactive
Along with using straps, we first make sure we use an engineered locking pin and ensure the winds are low before servicing the blades.
Below is an example found in news article about another site, which may help
Best Practices – HigginsNew, safer method of rigging halves time for ACC gearbox change-out
Best Practices AwardChallenge. Walter M Higgins Generation Station has a 40-cell Hamon air-cooled condenser (ACC) with 34-ft-diam Howden fans. The Flender gear reducers are driven by Teco-Westinghouse two-speed, 200-hp motors.
When changing an ACC gear reducer, the hub and blade assembly usually is disconnected as a unit and held in position by rigging and come-alongs or chain falls. Such rigging work can be a challenging process with safety implications. Fact: Rigging to the fan blades/hub assembly is never straight, in-line, or perpendicular to anything because of the nature of the equipment and structure.
During the installation of the new or replacement gear reducer, aligning the fan hub assembly to the gear reducer hub is difficult at best (Figs 1, 2). Since the rigging and come-alongs/chain falls are not directly supporting the assembly, adjusting any of them results in the assembly moving in strange ways.
Solution. After much discussion and several gear-reducer changes, the mechanical maintenance crew determined there had to be a better way to hold the hub and blade assembly to facilitate replacement (Fig 3). A basic design was drawn up and presented to NV Energy’s corporate engineering staff for review. After the design was finalized and engineered for safety and load, the project was handed out for fabrication.
The plant’s concept was simple and direct. Two cross members fit into the structural elements of the fan bridge and lock down with high-strength “C” clamps. Four 1¼-in. B-7 alloy high-tensile-strength all-thread rods drop down into the cross beams to hang over the hub plate (Fig 4). Four custom-designed clamps fit onto the hub plate and clamp securely to the plate, while the all-thread rods are through-bolted to the clamps and tensioned (Fig 5). The nuts on the top cross beam are then tensioned as well, locking the whole blade assembly in one position.The gear reducer is then unbolted and removed. The fixture is now holding the entire blade assembly securely and stable (Fig 6). Once the new or replacement gear reducer is dropped into position it is a simple matter of turning the input shaft to align the bolt holes on the fan hub assembly.
Note the center eye bolt in Fig 7. It is for the chain fall that actually removes the gear reducer from operating position and takes it outside for transfer to ground. The arrangement of eye bolts gives a clear and safe way to change from one hoist to another, without binding, confusion, or risk of rigging failure. Since the fan assembly has not moved at all during the gear-reducer change, it becomes a very quick, safe, and easy job.
Results. The fixture saved approximately two hours the first time it was used to change a reducer. There was a strong up-draft through the ACC cell during the change out and the fixture held firm and didn’t wobble or twist at all. In fact, in adjoining cells the fans were being turned by the wind to equivalent high rpm.
In conjunction with the gear-reducer fixture the entire gear-reducer change-out time has been reduced from a two-day event (working day shifts only) or about 20 hours, to a single 10-hr day job. The gear-reducer fixture increased safety and improved rigging height issues for removal of reducer from the fan deck of the ACC as well. -
January 23, 2017 at 12:48 pm #1650yefimParticipant
Many thanks to all who responded. You inputs were very helpful!
-
January 31, 2017 at 3:35 pm #1654Desmond de HaanParticipant
I know there are dedicated anti-rotational devices available for smaller units, ie ACHE’s. I do not believe there are devices or solution specifically designed for ACC’s.
-
January 31, 2017 at 5:46 pm #1655ctboxesParticipant
Hansen offers a hydraulic braking system applied to the gearbox high speed coupling, but it must be ordered with a new gearbox. This system is removeable so it can be used on other gearboxes as well.
-
February 1, 2017 at 5:20 am #1656udhay61Participant
Dear All,
In the maintenance platform also we have wooden reaper to support the fan hub as well as clamping the fan blades in opposite points with a clamps will help. That clamps will be locked with chains under LOTO system also. FYIP.Regards
-
-
AuthorPosts
- You must be logged in to reply to this topic.