  • in reply to: Finned Tube Airside Cleaning Document #2003
    udhay61
    Participant

    Hello Andy,
    Good Wishes
    I am also interested , sorry late, still request you to send the draft please.
    udhay61@yahoo.co.in
    bv.udhay@sravanthigroup.com

    Thanks . Kind regards. Udhayakumar

    in reply to: ACC Leak/Performance Issue #1734
    udhay61
    Participant

    Hi
    Hope you have taken all possible steps to locate the leaks , nice. One clarification is required whether checked the connecting pipe between the air evacuation header running in the top near the ST Exhaust duct . There will be minimum 2 to 4 connecting pipes for each module. Sometime found cracks in that causing vacuum drop. Also exactly in the ST exhaust penetrating portion sealing portion also gave problem. All syphon loops, vacuum breaker etc maybe checked. Thanks.Regards

    in reply to: ACC fan drive #1657
    udhay61
    Participant

    Dear All,
    Good Wishes..Only the issue is air flow path fouling, maintenance will be a difficult as approach issue. Safety under the ACC area to be taken care. Regards

    in reply to: Locking fans for safety #1656
    udhay61
    Participant

    Dear All,
    In the maintenance platform also we have wooden reaper to support the fan hub as well as clamping the fan blades in opposite points with a clamps will help. That clamps will be locked with chains under LOTO system also. FYIP.Regards

    in reply to: DEAERATOR TRAYS #1526
    udhay61
    Participant

    Yes, Deaerator trays MOC is 430SS .